Length or Span to Depth Ratio for beam and slabs - Printable Version
+- Front Desk Architects and Planners Forum (
https://frontdesk.co.in/forum)
+-- Forum: Architecture and Planning (
https://frontdesk.co.in/forum/forumdisplay.php?fid=1)
+--- Forum: Study Resource (
https://frontdesk.co.in/forum/forumdisplay.php?fid=114)
+---- Forum: Structural Elements of Building (
https://frontdesk.co.in/forum/forumdisplay.php?fid=90)
+---- Thread: Length or Span to Depth Ratio for beam and slabs (
/showthread.php?tid=3650)
Length or Span to Depth Ratio for beam and slabs -
Manish Jain - 12-20-2023
For RCC Structure
According to clause 23.2.1 of IS 456-2000
The vertical deflection limits may generally be assumed to be satisfied provided that the span to depth ratios are not greater than the values obtained as below:
a) Basic values of span to effective depth ratios for spans up to 10 m:
Cantilever : 7
Simply supported : 20
Continuous : 26
b) For spans above 10 m, the values in (a) may be multiplied by 10/span in metres, except for cantilever in which case deflection calculations should be made.
c) Depending on the area and the stress of steel for tension reinforcement, the values in (a) or (b) shall be modified by multiplying with the modification factor obtained as per Fig. 4.
d) Depending on the area of compression reinforcement, the value of span to depth ratio he further modified by multiplying with the modification factor obtained as per Fig. 5.
For two way slab of shorter span (up to 3.5 m) with mild steel reinforcement, the span to overall depth ratios is given below may generally be assumed to satisfy vertical deflection limits for loading class up to 3 kN/m2
Span span/depth ratio for Mild Steel span/depth ratio for HYSD bars
Simply Supported 35 28
Continuous Slab 40 32
For Steel Structure :
It is convenient to remember that serviceable steel section depths are in the range of ½” of depth for each foot of span (L/24). Some people might find it
easier to remember the following simplified rule where the length is expressed in feet and the depth of the member in inches:
Depth of Roof Beams, Roof Joists = 0.5*Length
Depth of Floor Beams, Floor Joists = 0.6*Length
Depth of Composite Beams = 0.55*Length