Cooling load for various Building based on rules-of-thumb
(Croome and Roberts, 1981)
Sl.no Application Required cooling load (TR) for 1000 ft2 of floor area
1. Office buildings:
3. Hotels
6. Banks 4.5 – 5.5 TR
7. Theatres & Auditoriums 0.07 TR per seat
The average cooling load in W® / m2 of air conditioned floor area are shown below for thirty different configuration of multi-storey office . The values have been computed for
(Croome and Roberts, 1981)
Sl.no Application Required cooling load (TR) for 1000 ft2 of floor area
1. Office buildings:
- External zones 25% glass: 3.5 TR
- 50% glass: 4.5 TR
- 75% glass: 5.0 TR
- Internal zones 2.8 TR
3. Hotels
- Bedrooms
- Single room: 0.6 TR per room
- Double room: 1.0 TR per room
- Restaurants 5.0 – 9.0 TR
- Basement & ground floors 4.5 – 5.0 TR
- Upper floors 3.5 – 4.5 TR
6. Banks 4.5 – 5.5 TR
7. Theatres & Auditoriums 0.07 TR per seat
The average cooling load in W® / m2 of air conditioned floor area are shown below for thirty different configuration of multi-storey office . The values have been computed for
- 1000m2 square floor
- 50% glazing
- Solar shading factor of 0.425
- Population density = 10m2 /person
- Electric load = 32 W / m2
- Outside air = 5 L / s. per person
To Read More.. http://frontdesk.co.in/building-services...ditioning/