MAXIMUM PERMISSIBLE NUMBER OF SINGLE CORE CABLES UP TO & INCLUDING 1100V THAT CAN BE DRAWN INTO RIGID STEEL CONDUITS (as per NBC-2016)
[Image: image-4.png]

According to the NEC-2017, the maximum fill for a conduit is:
One wire: 53% of the conduit's space
Two wires: 31%
Three or more wires: 40%

for more detail visit .... Electrical drawing of building